Devices > Remote Devices > Emerson ROCPlus EIE > UIS Command Component Parameters

UIS Command Component Parameters

The following tables list and describe the parameters specific to the UIS command component types for this remote device:

For more general information about UIS command component parameters, see UIS Command Components. The DG_F_DEV (Get data group from device) and DG_T_DEV (Send data group to device) command component types are configured in the template file. The other command component types are considered ‘special’ and are defined in the EIE editor code. See Special UIS Command Component Types for more information.

CLRHSTXA

Clear All History Tx Info clears all historical data group caches. CLRHSTXA has no command parameters.

Note: If you clear all caches using a UIS command, the cache values in each transaction of historical data groups are not reset; past transactions continue to display actual values. This is done for performance reasons so that each DDS transaction does not have to be updated. The driver ignores these cached values after the command has been issued.

CONFIG

Get RTU Configuration retrieves configuration information from the field device. CONFIG has no parameters.

CYUPDTPT

Update CygNet Point updates the record for a CygNet point. CYUPDTPT has the following command parameters:

Parameter Required Description

FOnErr

No

Fail cmd on update error indicates to abort the UIS command if any update errors are encountered. The errors that might come up include: if the point specified in the Fac, Serv, Site, or UDC parameters does not exist, or if the point exists in a different UIS and any messaging errors or communication failure to that service comes up.

Fac

Yes

Facility for pt identifies the facility of the point to update.

Serv

No

Service for pt identifies the SERVICE of the point to update.

Site

No

Site for pt identifies the SITE of the point to update.

UDC

Yes

UDC for pt identifies the UDC of the point to update.

UType

No

Update type indicates the type of update. Value options are 0 - 3, where 0=Completion, 1=Success, 2=Failure, 3=Creation.

UsrMsk

No

User bit mask specifies the user bit mask of the point to update.

UsrVal

No

User bit value to match specifies the user bit value to match when updating the point record.

Value

No

Value indicates the point value to update.

CYWAITPT

Wait for CygNet Point signals the UIS to wait to perform a command until the value of the specified CygNet point changes to a specified value.

CYWAITPT must be the first command component added to a UIS command. You cannot add other instances of CYWAITPT to a UIS command.

CYWAITPT has the following command parameters:

Parameter Required Description

Dur

Yes

Duration is the amount of time (in HH:MM:SS or HH:MM or HH) for the UIS command to wait for the point value to change before timing out.

FOnErr

No

Fail on point error indicates to abort the UIS command if any error conditions are encountered. The point errors that might come up include: if the point specified in the Fac, Serv, Site, or UDC parameters does not exist, or if the point exists in a different UIS and any messaging errors or communication failure to that service comes up.

Fac

Yes

Facility for pt identifies the facility of the point on which to wait for the point value to change before performing the UIS command.

Int

Yes

Interval indicates the frequency (in HH:MM:SS or HH:MM or HH) with which the UIS will check the point’s value to see if it has changed.

Serv

No

Service for pt identifies the SERVICE of the point on which to wait for the point value to change before performing the UIS command.

Site

No

Site for pt identifies the SITE of the point on which to wait for the point value to change before performing the UIS command.

UDC

Yes

UDC for pt identifies the UDC of the point on which to wait for the point value to change before performing the UIS command.

UsrMsk

No

User bit mask specifies the user bit mask on which to wait for the status bit change before issuing the UIS command.

Note: The user status bit parameters (UsrMsk and UsrVal) only apply to the extended status field of the point record, so they will not match anything in the base status.

UsrVal

No

User bit value to match specifies the user bit value to match before issuing the UIS command.

Value

No

Value to match specifies the value on which to wait for the point to change to before issuing the UIS command.

Note: You can set parameters for both the point user status AND point value. So you can match either one by itself, or you can specify that both must match your parameter values.

DG_F_DEV

Get data group from device retrieves a data group from a field device. The Parent XML Element is uccRecvParms. The following parameters are available for each specified data group type.

Data Group Type Parameter Required Description

Alarm800

EDate

No

Ending Contract Date defines the ending contract time and date for a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

No

Starting Contract Date defines the starting contract time and date for a date-range request.

Value options are strings in formats described in Selecting Date and Time.

ConOpCode

Cnt

Yes

Number of Locations defines the number of table entries to include in the "Configurable Opcode Data" data group.

Value options are integers from 1 to 44. Starting location + number of locations must be less than or equal to 44.

Val1

Yes

Starting Location defines which table entry to begin with when generating table entries for the "Configurable Opcode Data" data group.

Value options are integers from 1 to 44. Starting location + number of locations must be less than or equal to 44.

EventsLog

EDate

No

Ending Contract Date defines the ending contract time and date for a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

No

Starting Contract Date defines the starting contract time and date for a date-range request.

Value options are strings in formats described in Selecting Date and Time.

FmsAlarm

EDate

Yes

End Device Date/Time defines the ending device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

Yes

Start Device Date/Time defines the starting device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

FmsEvent

EDate

Yes

End Device Date/Time defines the ending device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

Yes

Start Device Date/Time defines the starting device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

FmsHistDGm

EDate

Yes

End Device Date/Time defines the ending device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

Yes

Start Device Date/Time defines the starting device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

FmsHistDGq

EDate

Yes

End Device Date/Time defines the ending device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

Yes

Start Device Date/Time defines the starting device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

FmsHistHGm

EDate

Yes

End Device Date/Time defines the ending device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

Yes

Start Device Date/Time defines the starting device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

FmsHistHGq

EDate

Yes

End Device Date/Time defines the ending device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

Yes

Start Device Date/Time defines the starting device date and time of a date-range request.

Value options are strings in formats described in Selecting Date and Time.

Hist800

SDate

No

Date defines the starting date and time for a "History – Daily/Periodic for Day" data group.

Value options are strings in formats described in Selecting Date and Time.

HistMultiD

EDate

Yes

Ending Date defines the ending date and time of a date-range request for row-based daily history for multiple points.

Value options are strings in formats described in Selecting Date and Time.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

For more information, see History Retrieval Optimization.

NumHistPt

Yes

Number of Hist Pts defines the number of history points to be retrieved. Value options are integers from 1 to 200, which is the maximum number of history points in a segment. The combination of Starting Hist Pt and Number of Hist Pts should not exceed 200.

SDate

Yes

Starting Date defines the starting date and time of a date-range request for row-based daily history for multiple points.

Value options are strings in formats described in Selecting Date and Time.

StHistPt

Yes

Starting Hist Pt defines the beginning of the range of history points to be retrieved. Value options are integers from 1 to 200, which is the maximum number of history points in a segment.

HistMultiM

EDate

Yes

Ending Date defines the ending date and time of a date-range request for row-based minute history for multiple points.

Value options are strings in formats described in Selecting Date and Time.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

For more information, see History Retrieval Optimization.

NumHistPt

Yes

Number of Hist Pts defines the number of history points to be retrieved. Value options are integers from 1 to 200, which is the maximum number of history points in a segment. The combination of Starting Hist Pt and Number of Hist Pts should not exceed 200.

SDate

Yes

Starting Date defines the starting date and time of a date-range request for row-based minute history for multiple points.

Value options are strings in formats described in Selecting Date and Time.

StHistPt

Yes

Starting Hist Pt defines the beginning of the range of history points to be retrieved. Value options are integers from 1 to 200, which is the maximum number of history points in a segment.

HistMultiP

EDate

Yes

Ending Date defines the ending date and time of a date-range request for row-based periodic history for multiple points.

Value options are strings in formats described in Selecting Date and Time.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

For more information, see History Retrieval Optimization.

NumHistPt

Yes

Number of Hist Pts defines the number of history points to be retrieved. Value options are integers from 1 to 200, which is the maximum number of history points in a segment. The combination of Starting Hist Pt and Number of Hist Pts should not exceed 200.

SDate

Yes

Starting Date defines the starting date and time of a date-range request for row-based periodic history for multiple points.

Value options are strings in formats described in Selecting Date and Time.

StHistPt

Yes

Starting Hist Pt defines the beginning of the range of history points to be retrieved. Value options are integers from 1 to 200, which is the maximum number of history points in a segment.

PerHst

EDate

Yes

Ending Date defines the ending time and date for a periodic history date-range request.

Value options are strings in formats described in Selecting Date and Time.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

For more information, see History Retrieval Optimization.

SDate

Yes

Starting Date defines the starting time and date for a periodic history date-range request.

Value options are strings in formats described in Selecting Date and Time.

PerHstD

EDate

Yes

Ending Date defines the ending time and date for a periodic daily history date-range request.

Value options are strings in formats described in Selecting Date and Time.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

For more information, see History Retrieval Optimization.

SDate

Yes

Starting Date defines the starting time and date for a periodic daily history date-range request.

Value options are strings in formats described in Selecting Date and Time.

SingleTlp

DataType

Yes

Data Type defines the type of data stored at the specified register number.

Value options appear in the Data Type drop-down menu in the Single Register data group dialog box.

FacUdc

No

Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT).

Value options are strings that specify a Facility.UDC combination.

TLP

Yes

T,L,P (one-based) defines the Point Type, Logical, Parameter combination to be retrieved from the device. Value options are integers, separated by commas, in the form T,L,P. The Point Type (T) portion of the value can be any valid point type on the device. The Logical (L) portion of the value is one-based and can be any valid logical for the specified point type. The Parameter (P) portion of the value can be any valid parameter of the specified point type.

TLPDesc

No

TLP Description provides for a user-defined description of the TLP in the event that the user does not want to use the default description. Value options are alphanumeric characters.

TxHist

EDate

Yes

Ending Date defines the ending date and time of a date-range request for historicized transactional data on a per-transaction set basis.

Value options are strings in formats described in Selecting Date and Time.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

For more information, see History Retrieval Optimization.

SDate

Yes

Starting Date defines the starting date and time of a date-range request for historicized transactional data on a per-transaction set basis.

Value options are strings in formats described in Selecting Date and Time.

WMEvtLog

EDate

No

End Date defines the ending date and time for a date-range request.

Value options are strings in formats described in Selecting Date and Time.

SDate

No

Start Date defines the starting date and time for a date-range request.

Value options are strings in formats described in Selecting Date and Time.

Back to top

DG_T_DEV

Send data group to device sends a data group to a field device. The parent XML Element is uccSendParms. The following parameters are available for each specified data group type.

Data Group Type Parameter Required Description

AO800Send

Val1

Yes

Auto Value defines a current value for the "Analog Output - Auto Value" data group.

Value options are floating-point numbers.

ConOpCode

Item

Yes

Table Item # defines which table entry a value is sent to in a "Configurable Opcode Data" data group.

Value options are integers from 1 to 44.

Value

No

Value defines a value to be sent to a "Configurable Opcode Data" data group.

Value options are determined by the table entry type and can be integer, string, or others.

DO800SAO

Val1

Yes

Auto Output defines the auto output value to send to the field device.

Value options are Boolean.

DO800SEU

Val1

No

TDO EU Value enables you to set the timed discrete output engineering unit value.

Value options are floating-point numbers.

Login

AccLevel

No

Access Level defines the security access level assigned to the corresponding operator ID.

Value options are char values 0 - 5.

OpID

Yes

Operator ID defines the identifier of an operator.

Value option is a user-defined string.

Password

No

Password defines the password assigned to the corresponding operator ID.

Value options are integers from 0 - 9999.

SingleTlp

DataLen

No

String Length specifies the string length of data stored at the specified register number.

DataType

Yes

Data Type defines the type of data stored at the specified register number.

Value options appear in the Data Type drop-down menu in the Single Register data group dialog box.

FacUdc

No

Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT).

Value options are strings that specify a Facility.UDC combination.

TLP

Yes

T,L,P (one-based) defines the Point Type, Logical, Parameter combination to be retrieved from the device. Value options are integers, separated by commas, in the form T,L,P. The Point Type (T) portion of the value can be any valid point type on the device. The Logical (L) portion of the value is one-based and can be any valid logical for the specified point type. The Parameter (P) portion of the value can be any valid parameter of the specified point type.

TLPDesc

No

TLP Description provides for a user-defined description of the TLP in the event that the user does not want to use the default description. Value options are alphanumeric characters.

Value

Yes

Value defines the value of the TLP.

GETTIME

Get RTU Time retrieves time from the field device. GETTIME has no command parameters.

SETTIME

Set RTU Time sets time for the field device. SETTIME has no command parameters.

STATUS

Get Current Status retrieves current status from the field device. STATUS has no command parameters.

TXHISTRG

This command is only exposed in the Emerson ROCPlus EIE template file. The parent XML Element is specCmds.

 

Parameter Required Description

TxSet

Yes

Transactional History Trigger defines a transaction set numeric ID, each of which corresponds to an Emerson transaction set numeric ID. Up to 10 transaction sets can be available, containing up to 100 transaction points each.

One TxSet parameter is required for each transaction set trigger you want to initiate from CygNet. You can use a UIS Command Button in CygNet Studio or some other mechanism for manually triggering a transaction, but you cannot trigger a transaction from a transactional data group editor dialog box in the Device Definition Service (DDS).

If you want to maintain a record of transaction set triggers initiated from CygNet, you must instantiate a "Transactional History Trigger" data group for each applicable transaction set. Records of CygNet-initiated triggers cannot be viewed as DDS transactions without this data group, although fields in the "Transactional History Cfg" data group editor(s) reflect the number of transactions.

Value options are 1 - 10 where each value represents a single transaction set. Multiple TXHISTRG command components can be added to a single UIS command.

This UIS command component and its parameters are only exposed in the Emerson ROCPlus EIE template file in the specCmds element.

Emerson RocPlus XML Example

<specCmds visible="true" canBeScheduled="true" clientCanInvoke="true" inheritsSecurity="true">

<TXHISTRG niceName="Transactional History Trigger">

<uccParms>

<TxSet desc="Transaction Set" type="ui1" required="true" rangeLow="1" rangeHigh="10" ordinal="0"/>

</uccParms>

</TXHISTRG>

</specCmds>

Back to top